In this post I have explained a relay cut-off circuit which may be included in inverters to ensures that under a no load at the output the condition is quickly detected and the supply cut off, preventing the inverter from operating unnecessarily. The idea was requested by Mr. Rajath.
Technical Specifications
I need to adopt a no load auto cutoff system into my inverter, do you have any suitable design, which could help me. or else can you give any idea on how to achieve ,as i need to shut down the output of the inverter when ever there is no current drawn from it. please help me ,here.
Regards Rajath
The Design
In a few of ay previous posts we have learned how to make overload cut off circuit such as:
Low Battery Cut-off and Overload Protection Circuit.
Motor over current protector circuit
However, the present concept deals with an opposite situation wherein a no load condition is supposed to be detected and cut off for persisting, that is I have explained a circuit for preventing a no load condition for inverters.
As shown in the above figure, a no load detector and cut of procedure can be initiated by incorporating this design in any inverter circuit.
The operational details may be understood with the following explanation:
The circuit comprises two stage, namely the current amplifier and sensor stage using the T3/T4 Darlington pair, and a simple delay ON stage using T1, T2 and the associated components.
As soon SW1 is switched ON, the delay-ON timer counting is initiated through C1 which begins charging via R2 and D5 keeping T1 switched off in the process. With T1 switched T2 is switched ON which in turn switches ON the relay.
The relay enables the positive from the battery to get connected with the inverter so that the inverter is able to start and generate the required AC mains to the intended appliances.
With the presence of a load at the output the battery undergoes a proportionate amount current consumption, and in the course Rx experiences a current flow through it.
This current is transformed into a proportionate amount of voltage across Rx which is sensed by the T3/T4 Darlington pair and it is forced to switch ON.
With T3/T4 switched ON, C1 is instantly inhibited from getting charged, which leads to an immediate disabling of the delay ON timer, making sure that the output of the inverter continues to supply the voltage to the load.
However, suppose the output of the inverter is devoid of any load (no load condition), T3/T4 is then unable to switch ON, which allows C1 to get charged gradually until the potential across it becomes sufficient to trigger T1.
Once T1 is triggered, T2 is cut off and so is the relay. With the relay contacts cut off and shifted from N/O to the N/C contact, the positive to the inverter is also cut off, the system comes to a stand still.
yusuf says
if the load current is say 10am,what will be the wire gauge from the base of t3/t4 and the +terminals of the base? I am really confuse sir
Swagatam says
wire gauge is not important for T3/T4 base….it can be any thin wire.
Amos Nyeneime Dominic says
Please can you assist me with 24volt 2kva inverter circuit with full protection?
Swagatam says
you can try the first diagram from the following article:
https://www.homemade-circuits.com/inverter-circuit-with-feedback-control/
First try this basic diagram, if you succeed then you can upgrade this to 2kva
Mahasetra says
Hello, thank you for your diagram, it is very enriching. I would like to use it to automatically turn off a solar inverter when not in use (no load). Do I have to choose a high-current relay if I plan to draw about 100A from the battery when the inverter is on? Thank you in advance
Swagatam says
Thank you, yes the relay contact current rating should be ideally two times more than the intended maximum load current
sir says
hello sir
i try this circuit but when i disceonect the load and connect it again the relay dosnt switsh on
Swagatam says
The load should be high enough to create at least 1 V across Rx and enable T3/T4 conduction. If this does not happen, the relay will not activate
sir says
Hello Sir
-The battery is a12V 8Ah lithium ion
-The inverter is 12 TO 220V based on transistor astable 60Hz circuit with 2 irf640 mosfet connected to 300 watt center tape toroidal transformer
-The minimum load is 220V 9W bulbs consuming 0.340 A
-The system consume 0.16A with no load connected
-The system consume in total with the bulb connected 0.5 A
+what i need :
-The relay to switch on every time i switch on the bulb
-The relay to switch off every time i switch off the bulb
How i can make the circuit work with this system ?
Godfrey says
Hello sir pliz help me build a1500watts inverter,I have no idea on how to make one, pliz show me the simplest circuit
Swagatam says
Hello Godfrey, you can select any inverter circuit presented in this website and replace the MOSFETs with two parallel IRF540 for each channel. For battery use a 24 V 300 Ah battery, make sure to operate the oscillator circuit through a 7812 IC, and replace the transformer with a 24-0-24v, 70 amp transformer
Nikhil says
Hi,
I think for battery-powered applications relays are not a good choice, because of high coil current when energized. Can you suggest a good efficient replacement?. My considerations are p-channel power MOSFET or solid-state relays.
Thanks
Nikhil
Swagatam says
Hi, a relay is much better since it will allow the inverter to work with 100% battery power. The coil consumption will be negligible, may be 1 or 2% of the total inverter consumption. A MOSFET or SSR will dissipate energy causing the inverter to work with lower efficiency.
Nikhil says
Thank you, sir, for the reply.
I have one more doubt.
There is a chance for a slight increase in the voltage of a battery when a load is disconnected from the battery. Due to this, there is a chance for the relay to switch on again if the no-load battery voltage is above cut-off voltage. So a couple of switchings will occur before a stable state is reached.
Is this possible ?.
if possible, then how to solve this?.
Thanks & regards,
Nikhil
Swagatam says
Thanks Nikhil, The circuit is not voltage dependent, it’s current dependent. Voltage fluctuations will not affect the relay circuit, its the load current that will affect the circuit.
Apurva deepak says
Because there has no center tape transformer will be used for output supply
Swagatam says
You can try this:
https://www.homemade-circuits.com/2014/01/simplest-full-bridge-inverter-circuit.html
This is the only recommended design
Engr bashir says
ok Sir i will let u now when i am done
Engr bashir says
CORRECTIONS
Rx=0.2/0.4(400mA) =0.5ohm
hence 0.2x5A=1watt
therefore Rx=0.5 ohm 1 watt
did i do it correct??
Swagatam says
yes that looks OK to me, use a wirewound type resistor preferably.
Engr bashir says
That mean 0.5x5A=2.5 watt, therefore =0.5ohm 2.5watt resistor?? OR
0.5x 10A=5 watt, therefore =0.5ohm 2 watt resistor??
Swagatam says
It is not 0.5V it is 0.2 or 0.3V, please check again….
Engr bashir says
ok sir as i did calculate it here
0.2/0.2=1ohm resisor,
0.2x.0.2=0.04 watt
That mean my resistor current must be 0.04watt am i correct???
Swagatam says
it should be:
Rx = 0.2/0.4 (400 mAmps) = 0.5 ohms
wattage = 0.2 ohms x inverter maximum current.
inverter maximum current could be 5 amps or 10 amps as per inverter wattage
Engr bashir says
GOOD MORNING SIR, i hv made this circuit today but the problem is that the Rx resistor is burning why?? it is 1 ohm 1/4w Check the image here
https://mobile.facebook.com/photo.php?fbid=1835553799874433&id=100002594924040&set=p.1835553799874433&source=47&ref=opera_speed_dial_freefb&__tn__=R
Swagatam says
The formula for wattage will be: voltage drop across the resistor multiplied by the maximum current rating from the inverter battery.
Here the voltage across the resistor is supposed to be 0.2 or 0.3V, so multiply this by the maximum current draw of the inverter…..that will give you the wattage of the resistor.
Engr bashir says
thank u sir
Engr Bashir says
sir if i got you right that mean if my threshold is 400mA that mean i should calculate the Rx like this:- 0.2/0.2=1ohm resisor,
0.2x.0.2=0.04 watt
Swagatam says
It should be Rx = 0.2/0.4 = 0.5 ohms, in this case if the load is consuming below 400mA, the relay will switch OFF the inverter
Swapnil says
Sir
I need to construct the circuit to store combined electricity from solar and piezoelectric in battery and this battery will be used for inverter input .
It can be possible sir?
Swagatam says
Swapnil, how much voltage and current are you getting from your piezo source???
Techie says
Doesn’t make sense. Even if the inverter is off you are losing the power at Rx resister
Swagatam says
“losing power at Rx?” How? if the relay is switched OFF how will the inverter consume power??
Rick says
Hello Swagatam,
Everything is 100% clear now!
Thanks a ton for your time and dedication to explain the formula in detail.
Very much appreciated!
Success and regards,
Rick
Swagatam says
You are most welcome Rick!!
Swagatam says
sorry, the answer should be 0.02 watts
…however 0.1 amps cannot be considered for calculating the Rx wattage, because 0.1 is the minimum current value, we would want it to be multiplied with the max current limit, which could be say for example 2 amps.
so Rx wattage for this example would be 0.2 x 2 = 0.4 watts
Swagatam says
for example let's assume the current threshold to be 100mA
T3/T4 triggering potential to be 0.2V, the Rx will be
0.2/0.1 = 2 ohm
wattage will be 0.2 x 0.1 = 0.04 watts
Swagatam says
Hi Rick,
the formula for calculating RX is T3/T4 minimum triggering level divided by the desired current threshold, and the wattage will be the desired current threshold multiplied by the triggering level.
I hope you got the relationship
Rick says
Hi Swagatam,
Trying my luck again…
Ohms value calculation of Rx is clear, but what about Watts?
Thanks for your help,
Rick
Swagatam says
Hi Rick, I have clarified it in the above comment….
Gilligan says
Thank you for your reply. Do you sell parts? If not, do you have a parts list?
Swagatam says
sorry I don't sell parts
the parts are already specified in the diagram, please click to enlarge it, and copy down the numbers as mentioned in the diagram…all the parts are standard type and does not need any consideration.
Gilligan says
Hi, I came across this post and the concept of your circuit is exactly what I am looking for. I have a 4k 110v AC inverter powered by 4 6v batteries wired in series for 12v. The inverter has a power saver mode built in (25 watts) but it will sense and turn on my 110v AC refrigerator. However, when I open the door, the light bulb is enough to trigger the inverter to power on. Also, the power sensor pulses every 3 seconds which I'm afraid might damage the compressor. So my question is, is the load in your circuit adjustable and how would I do that to sense a low load. Thank you in advance for your reply.
Swagatam says
Hi, the resistor Rx value can be altered as per the required specifications, and the inverter can be enabled to switched ON or OFF at any desired load conditions. Higher values will allow the inverter to operate with higher loads only and vice versa,
Bady Badru says
hellow sir i have this 60watts inverter what will be the value of Rx at full load and how can i obtain this minimum load current?
Swagatam says
hello Bady, you can use the same value that's indicated in the diagram.
Bady Badru says
hello sir, i would like to ask some few question about this project
1)the darlington transistor are connected at the negative terminal of the battery how is that possible to work? i cant a clear picture about the current flow of this circuit
2)if there are designing calculation for the circuit analysis pleas help me with them
thanks in advance
Swagatam says
hello Bady, the Rx resistor needs to be in series with the supply, regardless of the position a voltage will be developed across it whenever the load is switched ON, in the shown design since the current is entering from top of the Rx, the (+) voltage is developed at the base of the associated T3 transistor.
Summon Skull says
Can this circuit work along side your Low Battery Cut-off and Overload Protection Circuit on an inverter, since both circuits would be on the dc side of the inverter.
Swagatam says
yes both can work together, the second sensing resistor could be added in series with the above Rx for sensing overload.
Angelous Chavez says
your welcome sir.
What is the purpose of the Rx?
what is the right value for the Rx sir?
Swagatam says
Rx is for generating the triggering voltage for the associated Darlington transistor
Rx could be 0.2/1amp = 0.2 ohm
Angelous Chavez says
Sir, one more question what will be the the value of Rx?
I don't have an idea about that hope you could help me.
Thanks in advance…
Swagatam says
Angelous, The formula for evaluating Rx is given in the diagram..
Angelous Chavez says
Sir what a really good circuit.
When this circuit conected to the inverter, it can't affect the efficiency and working performance of the inverter?
Swagatam says
Thanks Angelous, No it will not affect the inverter performance…
Chandan Parashar says
dear swagatam,
i have a 10 kv inverter wih 15 batteries ie , 180volts.
can you suggest me the switch, relay and Rx rating
Swagatam says
dear chandan,
10000/180 = 55 amps, therefore the switch and the relay wil need to be rated at 60 amp minimum…T2 will need to be upgraded to TIP122
Rx will depend upon the intended minimum wattage at which the inverter may be required to be operative.
mexzony says
Hello sir
Can I pass a weak pwm signal into a MOSFET driver like a tc4427 and then use it to drive another full bridge driver IC like the ir2110.
Basically can I drive a MOSFET driver with another MOSFET driver?
Swagatam says
no that won't be a good idea…I not able to simulate it in my mind.
mexzony says
By the way it will have a 24v supply for the inverter
mexzony says
Hello sir
Also I have been trying to see if I can come up with an overload/ surge circuit using the delay circuit concept above. Here what I intend to achieve
1) the circuit should have a standard 1500w (full load)reference current or voltage.
Then when we power up a load that is higher than 1500w say 1505w or 1550. As a matter of fact anything from 1501w, instead of indicating an overload immediately it should allow for a minimum amount of time maybe 10secs and then if the load is still at a wattage higher than 1500w it then trips off.
Remember I said I wanted surge ability for loads that require more starting current so now if we power a load that will go as high as say 3000w surge technically it is higher than 1500w and so the circuit delays tripping off overload signal for maybe as usual 10secs and then if after 10secs the load has not droped to its normal power consumption of say 500w then it trips off.
Hope you get what am trying to do here.
Am hoping the circuit can have like a reset button too.
Swagatam says
Helo Michael, you can incorporate any of the shown techniques in the following article, and add a 100uF capacitor across base/emitter of the transistor for the delay effect:
https://www.homemade-circuits.com/2014/06/simple-current-sensor-circuit-modules.html
mexzony says
Hello sir
For this delay circuit I can use a 24vdc input I will only increase the relay rating and double the value of the resistors to limit current?
I then use a 12v regulator to power the circuit after the relay.
Swagatam says
Hello Michael, that will do.
mexzony says
Hello sir
Sir if I input 24v to the lm338 and set an output voltage of 12v.if the voltage falls to 20v will the ouptut 12v from the regulator also fall?
Swagatam says
Hello Micheal, no that'll not happen…as long as the input is at least 3V above the set output voltage, you can be sure of the getting a constant voltage as per the set level.
mexzony says
Also sir
Pls what software do you use to draw those schematics?
Swagatam says
I use coreldraw
mexzony says
Hello sir
Question about gate resistors.
If I use say a 10 ohm resistor say for a push pull and I have just one resistor on each side.
Now if I parallel say 3 resistors on each side does that mean I use 30 ohm resistors for each mosfet so that the each three MOSFETs in parrell now have 10 ohm resistors when we use the parallel resistor formulae.
mexzony says
Also sir
How many IC's can a 780X regulator power at a time.
Swagatam says
Hello Michael,
you'll need to connect 10 ohm individual resistors in series with each gate of the mosfets…it does not have to be 30 ohms
780X are rated to deliver 1 amp…so you can can divide this with IC's current specs to get the
mexzony says
Hello sir
I am looking at this IC hip4081A it's a full bridge driver as I don't want to use two ir2110.
Sir do you have any experience with this driver?
It can give out up to 2.5A peak current.
Swagatam says
Hello Michael, I have not yet studied this IC so I won't be able to suggest much about its operational details, by the way did you check out its datasheet?
You can see it here:
https://www.intersil.com/content/dam/Intersil/documents/hip4/hip4081a.pdf
odudu johnson says
Morning sir, I am a final yr undergraduate am working on an automatic changeover switch with wireless generator control abilities.. Please I need information thankzzz….. oduduj@gmail.com
Swagatam says
Hi Odudu, please provide more info regarding your requirement, by the way i may be having this circuit already in my blog….
mexzony says
Hello Sir,
So if am right by your explanation then it means that
When the circuit is on T1 base voltage is grounded due to the capacitor charging and this allows a base voltage at T2 thereby switching it on and allowing the really to be switched on.
Now when load is significant voltage is present at T3 and T4 base which then halts the capacitor charging.
2) the delay time formulae is t = 1.1RC right?
3) I also noticed that C has to be large enough to effectively ground voltage at base of T1?
Swagatam says
Hello Michael,
yes that's correct, but a "significant" voltage or current is not required, the operation can be assumed to initiate even with a small load at the output, and that's what the circuit is intended to be like. This can be set by calculating Rx correctly.
I have not yet checked the formula, it could be correct, but is not important as the value of R2, C1 can be fixed with a little trial and error.
C does not have to be large, because we want the changeover to take place quickly so basically it should be relatively smaller.
mexzony says
Hello sir,
Nice and simple concept
I have a few questions though. While mind simulating the circuit I want to ask
1) "under signigicant load" when huge currents flow through Rx which converts to proportional voltage and then the Darlington pair(T3 and T4) is triggered with sufficient voltage at its base this should ground the voltage at the base of T1 which leads to having a voltage at the base of T2 which triggers T2 and therefore stops the relay from working right?
2) how will the capacitor trigger T1 though the diode
Swagatam says
Hello Michael,
thanks!
1) with T1 switched OFF, T2 is allowed to be switch ON, which in turn keeps the relay ON. The relay contacts in this situation connect across the N/O allowing the inverter to operate.
so in the presence of load, the relay is allowed to remain activated.
2) the capacitor while charging pulls the T2 base voltage to the ground level, until it has charged to a point where the base voltage at T1 is able to reach above the 0.6V mark, and at this point T1 switches ON.